PLC I/O 連線

2012-10-27 6:37 am
Automatic run/stop with a plc control. Auto/forward/backward Indicator is required.
參考此圖 http://i.imgur.com/DzEro.jpg
Sol A: 24V coil, another E.stop (NC) can be added to stop the cylinder immediately.
參考此圖 http://i.imgur.com/dTeHv.jpg

問題:PLC I/O 連線: (plc output module: relay type)

回答 (2)

2012-10-27 6:01 pm
✔ 最佳答案

圖片參考:http://imgcld.yimg.com/8/n/HA00639401/o/20121027093950.jpg


1。你的電路太簡單,完全不需要用到編程器PLC,而且編程器PLC價值不菲,除非你另有目的,不然還是不要改用編程器PLC。

2。你不能在這個電路内加任何的緊急停機開關,因爲就算你將電源切斷,那個氣缸/油缸(Cylinder)還是會收縮動作到頂底爲止,除非你改用雙控閥。

圖片參考:http://www.cylinder-hydraulic.com/wp-content/uploads/2009/10/cylinder_detail.jpg


圖片參考:http://i00.i.aliimg.com/photo/v0/355702190/Daikin_KSO_hydraulic_solenoid_valve.jpg


圖片參考:http://www.hshydraulic.com/products_img/2007724101563.jpg


圖片參考:http://www.1st-product.com/uploads/18/7691/solenoid-valve-530.jpg


圖片參考:http://www.supplierlist.com/prod_img/jelpc/79953_BMPUAM_Series_Solenoid_Valve.jpg


2012-10-27 10:23:18 補充:
如果你堅持要用PLC,I/O 接線如下


Com = +24V out
X0 = E. STOP - NC
X1 = Auto ON - NO
X2 = forward STOP = LS-1 - NO
X3 = backward STOP = LS-2 - NO

2012-10-27 10:23:30 補充:
Com = +24V IN
Y0 = emergency stop / immediately stop indicator lamp
Y1 = cylinder forward driver signal
Y2 = cylinder backeard driver signal
Y3 = forward indicator lamp
Y4 = backward indicator lamp


你還要寫編程,工程浩大啊。
2012-10-27 7:30 pm
你重點在那那都可隨便編
可見你...........作業
真是滴....不長進...連最基本滴你都不看