RCD 漏電斷路器問題

2010-01-03 9:19 am
請問RCD 漏電斷路器係點運作.點解會跳制.有咩用.

http://photo.pchome.com.tw/doramailzz/126245221629/

幫幫手解答.萬二分多謝

回答 (4)

2010-01-03 5:57 pm
✔ 最佳答案
請注意 : 你幅圖係錯既, 請參考雪地火花既圖



圖片參考:http://imgcld.yimg.com/8/n/HA00639401/o/701001030015013873390270.jpg



圖片參考:http://imgcld.yimg.com/8/n/HA00639401/o/701001030015013873390271.jpg



圖片參考:http://imgcld.yimg.com/8/n/HA00639401/o/701001030015013873390282.jpg




2010-01-03 10:00:58 補充:
因爲ZCT繞線方向錯佐,冇平衡作用而產生電流,所以會立刻跳制,明未?

2010-01-04 02:05:36 補充:
繼電器 = Relay

TRIP COIL 係 ACB 或 MCCB 内既 STC

當然 RCD 内都有TRIP COIL

2010-01-04 02:29:29 補充:
係佢划錯佐
應該係TRIP COIL
2010-01-05 7:25 am
to be clear,

in a L-N Circuit,since there are series wiring,so the current of L equal to The current of N.
when its leakage,some current pass through the earth,so the current of L and N are not equal.the mechanism had been detected,the RCD will break the circuit in atleast 0.4s.
2010-01-04 5:55 am
博士果然細心,抵讚!

2010-01-03 21:57:49 補充:
博士,TRIP COIL同繼電器有乜嘢唔同呢?
2010-01-03 10:34 am
RCD Residual - Current Device

RCD 是用一個差異電流變壓器, 偵測兩個導體之間電流平衡( 火線與中性線之間的電流差異), 如電流不平衡時候, Trip Coil 在25-40 微秒內切斷電流.


圖片參考:http://img264.imageshack.us/img264/3074/abc2w.jpg