1. Emergency Generator is classified as Fire Services Installation (FSI) and so it shall be maintanined in efficient working order at all times and shall be inspected by a registered fire service installation contractor at least once in every 12 months. Moreover, all units should be run once per month under load conditions for a period of not less tha 30 minutes. (You may refer to the CoP for Inspection, Testing and Maintenance of Installations and Equipment issued by FSD for details) (
http://www.hkfsd.gov.hk/home/eng/source/safety/testing_2005.pdf)
Regarding details of the tests to be performed, you may also refer to appendix 3 of the captioned CoP. (
http://www.hkfsd.gov.hk/home/eng/source/safety/appendices_2005.pdf)
2. For WR2 testing, inspection and etc., you may refer to Appendix 13 - Checklist 1 to 4 of EMSD's CoP for the Electricity (Wiring) Regulations. (
http://www.emsd.gov.hk/emsd/e_download/pps/pub/COP_E.pdf)
Hope i can reply to your queries.