三相摩打火牛開車起動變壓器其實要學習不難,我先比個簡單圖你研究,如果唔明白再問我,下面就係
圖片參考:
http://img165.imageshack.us/img165/3701/atstarterzm2.jpg
開始啓動時間如下:
按下“啓動”時,K3M先入,跟住就K2M入,當摩打既速度有75% ~ 80% 時,K3M退出,K1M再入,就完成佐。
Auto transformer Starter.
An Auto transformer starter uses an auto transformer to reduce the voltage applied to a motor during start. The auto transformer may have a number of output taps and be set-up to provide a single stage starter, or a multistage starter. Typically, the auto transformer would have taps at 50%, 65% and 80% voltage, enabling the motor to be started at one or more of these settings.
There are two ways of connecting an auto transformer starter, the most obvious way is to apply full voltage to the transformer via a contactor, and connect the motor to the tap by means of a contactor. When the motor has accelerated to full speed, or has run out of acceleration torque, the tap contactor opens, disconnecting the motor from the transformer and another contactor closes connecting the motor to the supply. The transformer can now be disconnected from the supply. This format is known as an open transition starter and is less than ideal due to the fact that the motor is disconnected for a short period of time during the start period. While the motor is connected and accelerating, there is a rotating magnetic field in the stator which causes flux in the rotor and thus a rotor current to flow. At the instant the motor is disconnected, there is a magnetic field in the rotor which is spinning with-in the stator winding. The motor acts as a generator until the rotor field decays. The voltage generated by the motor is not synchronised to the supply, and so on reconnection to the supply, the voltage across the contactor at closure can be as much as twice the supply voltage resulting in a very high current and torque transient. This open transition switching is often known as the auto-reclose effect as it yields similar characteristics to opening and closing a breaker on a supply to one or more motors. The consequences of open transition switching can be as bad as broken shafts and stripped gears.
2007-09-29 16:44:07 補充:
By a rearrangement of the power circuit, it is possible, at no extra cost, to build a closed transition starter and thereby eliminate the current and torque transients. The closed transition auto transformer starter is known as the Korndorffer starter.
2007-09-29 16:45:19 補充:
The open transition switching is achieved by reconnecting the tap contactor between the transformer and motor, to the star connection of the transformer, hard wiring the motor to the tap, and altering the sequence of contactor control.
2007-09-29 16:47:31 補充:
To start the machine, the main contactor and the star contactors are closed applying reduced voltage to the motor.
2007-09-29 16:48:16 補充:
When the motor has reached full speed, (or run out of acceleration torque) the star contactor is opened effectively converting the auto transformer starter into a primary reactance starter.
2007-09-29 16:48:56 補充:
Next the primary reactance is bridged by a contactor applying full voltage to the motor. At no time does the motor become disconnected from the supply.