1. use the megger tester (insulation tester). the probe connect against test core and common round ( earth wire or connected metal part). Inject 500 or 1000V by insulation tester, check the reading..
If reading is 0 M-ohm. Mean..the conductor is shock to ground.
If reading appear 1 M-ohm; mean the conductor have 1,000,000 ohm resistance between conductor to ground. The current leakage is less, general result is passed under government cable insulation test min. requirement.
2. if Switchboard..the method is similar..
3. HV cable, the tester voltage up to 10,000V and insulation at least 1G-ohm.
Note: do not forget core to core test due the full set cable testing.
2006-10-15 02:56:13 補充:
1. use the megger tester (insulation tester). the probe connect against test core and common gound ( earth wire or connected metal part). Inject 500 or 1000V by insulation tester, check the reading.. common ground